After a power outage, Logix5561 lost the program?
wendaiyu
Jun 2014
toronto
87
Hi, guys, how’s going?
Two weeks ago, after a power outage, Logix5561 lost the program, so we had to download the program to the controller.
Then we installed a new battery (which we bought 2 years ago). But the same issue still happened after a power flicker yesterday.
We checked the battery with multi-meter, it looks like OK, cuz there’s 3.2V on it.
Could somebody give us a hand to fix it?
Thanks a lot.
If battery fault led is on, it's not good. Why don't you write the program to nonvolatile and make the controller boot from there?
That's a Series B controller, since it has the CompactFlash slot on the front instead of the bottom.
The solid red BAT indicator is proof that the controller isn't being backed up by the battery, regardless of what the terminal voltage is.
My understanding is that the -BA2 battery had better performance and longevity to match the hardware of the Series B controllers. While they're both nominally 3.2V lithium batteries, A-B intentionally changed the connector so that Series B controllers would get the power they needed to meet the specs that were advertised.
A-B used a bright blue shrink wrap on the 1756-BA2 batteries; the one shown is probably aftermarket.
Maybe the pin assignments are wrong, or the connector is damaged internally, or there's something else wrong with the controller that's preventing it from properly receiving battery backup power.
The short term solution is to use a CompactFlash card to back up the program, and carefully evaluate the system to be sure it can survive the loss of current tag values because of the loss of volatile memory.
L81 series processor, DHRIOE 1756 card, communicating to some old PLC 5 IO. Site wide power outage after power up everything is okay except 1...
1,522
We had a power outage at a site and there are two machines that run their own instance of Wonderware Intouch 2017 SP3. With this power outage the...
1,564
I have a client that has many Automation Direct DL06 PLCs for a municipal water/wastewater system. When there is a power outage, one of the sites...
2,446
Hi there, I am having trouble with saving Data Log in Micro850 AB PLC. The data log requires date and time information to function properly...
2,161
This may not be the best place for this question, but I figured it was worth a shot. We have a factory that has frequent quick power failures...
1,653