Corrupted processor or Unknown Processor
George Graziano
Jul 2004
NY
447
Has anyone seen this before & found a way around it?
1747-L553 Processor. Working now with no problem, except I can't talk to or save the file. Battery light on. tried serial as well. No problems talking to /from Panelview (serial)
George
I have had similar issues in the past.
brown outs and sudden voltage spikes are an issue.
is there a surge suppressor in front of the plc power?
if not, you need to install one for the controls.
I would reset the plc to default condition and reload the program.I hope you have a good backup of the program.
james
Not sure it is the most resent one. It is working right now & communicating. But, if something happens I would have to load in what I do have.
George
It would be in your best interest to get a upload the current program.
the plc program is the master, someone could have made changes.
1. make a copy of what you have (you don't want to corrupt it).
2. use the backup copy and upload the current program from the plc.
3. save the program and go off line.
4. shut sown the pc, wait 30 seconds, and reboot. ( silly but I do it as insurance)
5. open the file you just uploaded to see if it opens.
6. insert a dummy rung and recompile the program.
7. save it.
8. reopen the file and delete the dummy dung.
you should be good to go.
james
That's the problem. I have tried going online by Serial & Ethernet. That is the error I get. I even tried to upload to an empty file.
George
If the Panelview can talk to it serially, then you should be able to do it that way too. Can you dig into the details of the Panelview comms settings. Maybe there is a difference between what is configured and what you have already tried.
Also, I can't view the image you posted...not sure if it is a forum glitch or other?
Tried sending the picture twice.
I will check the comm of the panelview Monday and make sure it matches and try that way.
There was a situation that could generate that alarm if the CPU was originally programmed with a certain 3rd party software...I forget the details.
Okie,
I remembered, I checked using serial as well & it gave me the same error. I will confirm on Monday, it is still talking to the Panelview. Also, will check and see if that is using messages to other processors.
George
Hi, we are using 5/04 processor and when we are going online it is showing the processor is communicated in RS Linx. When i select the processor...
2,212
I recently setup RSLOGIX 500 v6.10.10 on a new laptop running windows 7 pro. When I attempted to go online with a SLC5/05 via ethernet I get an...
2,945
I am trying to connect to a PLC but i'm getting the 'Corrupted Processor' error. I am using Logix500 v6.3 so I believe its out of date with the...
2,093
Hi all, We have a Allen Bradley SLC5/05 that has a fault light that is on constant and the remainder of the lights are flashing. Also, upon...
3,018
I am uploading the program from a SLC-5/04 and i am getting this message "CORRUPTED PROCESSOR". The plc is running with no problem, working fine...
3,271