Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration.

In star configuration, wouldn't the autotune of the drive shown strange values for magnatizing currenty and motor resistance?
 
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration.

In star configuration, wouldn't the autotune of the drive shown strange values for magnatizing currenty and motor resistance?
"Strange"? Not if that was what was done from the outset. The VFD doesn't have pre loaded values of what a motor SHOULD look like, it just knows what it has been told or what it learns in Autotune. Garbage in, garbage out.
 
The motor was mis-wired. It should have been wired delta, but was wired in star.

Would the magnatizing current be different in star then delta?
 
If the FLA of the motor was for delta and that was put into the VSD for motor max current and they were wired in star, l wouldn't have thought they would get to Delta FLA?
 
One thing that I can guess could explain this is star winding will give lower hp for motor. Since the motor is connected to a centrifugal pump, the pump power is a fx of speed. If the motor was not able to produce the needed HP for the pump speed, then the motor would be running slower than frequency demanded. This would mean that slip was much more than it should have been, with increased slip came increased current consumption.

Regardless, the drive was supposedly setup by a factory startup person. The motor winding connections should have been checked. The provider of the VFD (and the company that hired the startup person) is thinking they are going to invoice for 4hrs for supporting this since it wasn't a drive error. ....
 
So the VSD FLA were set to motor FLA? If yes l would agree that the motor in star couldn't get up to speed so between star winding start speed and max speed it could get under star winding, wasn't fast enough to bring the current down to star run current, so would stay overloaded between x1 >> x6 times, 0.58 of delta FLA
 
Last edited:
One thing that I can guess could explain this is star winding will give lower hp for motor. Since the motor is connected to a centrifugal pump, the pump power is a fx of speed. If the motor was not able to produce the needed HP for the pump speed, then the motor would be running slower than frequency demanded. This would mean that slip was much more than it should have been, with increased slip came increased current consumption.

Yes, the peak torque produced by the motor would be the square of the voltage difference. So the motor would be producing only 33% of it's rated peak torque, which is what it uses to accelerate the load. In a centrifugal pump, the load does not "couple" at a constant rate, it increases with speed. But the pump would still try to run at the programmed speed, meaning the load (flow) will try to be at design values. But the motor would be incapable of supplying enough torque to keep it there. That, as you mentioned, would cause it to increase slip and thereby try to draw more current, to the point of overloading itself. Motors are "dumb animals".

Regardless, the drive was supposedly setup by a factory startup person. The motor winding connections should have been checked. The provider of the VFD (and the company that hired the startup person) is thinking they are going to invoice for 4hrs for supporting this since it wasn't a drive error. ....
I get your point, but having done countless VFD startups, I have rarely checked the motor connections (unless I made them myself) because if I were to crack open the motor peckerhead, I now own the motor; no think you. Most of the time the motor is already connected when I arrive, I will basically assume the installer was competent enough to know what they were doing.

On a few occasions I have NOTICED the lack of performance and FOUND that the motor was incorrectly wired, so to that extent, I agree that if the system was able to operate under load, the VFD technician should have noticed. But that said, I have also been on MANY projects to start up the VFDs and the system is not ready to fully run, so I am provided with "simulated" loads, i.e. a fire hose supplying water to the pump. That can set up a tricky situation in that the dynamic head of the "test" is not the same as it will be in full operation, so you don't know what you don't know yet. In those cases I have learned to warn the users that this test setup may not be the final values, but contractors want to get paid, so they sign off on it. If I have to go back, it's at the expense of someone else.
 

Similar Topics

A 45 KW motor (440Vac, 3Ø, 60Hz, IFL=73.2 A) is having a contactor (for star & delta) rated at 22KW @ 440Vac and 1-set-of-14 mm2 THHN. (See...
Replies
19
Views
5,912
I have recently been given the problem of writing a programme for a PLC with 3 contactors KM1-star KM2-main KM3-delta with 2 push buttons PB1 stop...
Replies
6
Views
5,736
Here's a question I thought I'd never ask with all my 50 years of experience but I don't know - so I'm asking. I have to change a star delta...
Replies
23
Views
3,157
Hi all, Got a customer who's asked me to look at a new machine they've gotten in which they're having trouble starting. It's a brand new...
Replies
10
Views
4,281
Without going into a lot of detail, 150 hp motor with a Star/Delta Start how much time on Star before switching to Delta. This is a compressor, I...
Replies
14
Views
2,020
Back
Top Bottom