Star delta wiring
mcflynn1977
Feb 2005
Dublin Ireland
I have recently been given the problem of writing a programme for a PLC with 3 contactors KM1-star KM2-main KM3-delta with 2 push buttons PB1 stop PB2 start ,after pushing PB2 KM2 is energised and stays energised until PB1 is pressed the motor initially starts in star.
The programme must be dseigned in such a way that if KM1 is energised Km3 must be disabled and vice versa.
any suggestions greatly appreciated.
Dear mr. McFlynn.
This is an extremely basic problem to solve in a PLC program.
You should try to solve it youself. This because you do not learn anything from getting others to do your homework for you.
Even if you cannot solve it completely, a half-finished work that you have done yourself is MUCH better than a finished work you have just copied from others.
If you have some half-finished work, then we will gladly take a look at it.
mcflynn1977,
show us what u've got....
we'll show what we've got....
i cant determine your way to think, let us explore your ladder
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
2,629
A 45 KW motor (440Vac, 3Ø, 60Hz, IFL=73.2 A) is having a contactor (for star & delta) rated at 22KW @ 440Vac and 1-set-of-14 mm2 THHN. (See...
19
5,919
Here's a question I thought I'd never ask with all my 50 years of experience but I don't know - so I'm asking. I have to change a star delta...
23
3,162
Hi all, Got a customer who's asked me to look at a new machine they've gotten in which they're having trouble starting. It's a brand new...
4,293
Without going into a lot of detail, 150 hp motor with a Star/Delta Start how much time on Star before switching to Delta. This is a compressor, I...