Some AOI Hackery
JeremyM
May 2014
Dallas, Texas
1,233
We’re familiar with the basics of AOIs:
  • input, output, and in/out parameters are visible and usable by the program
  • local tags aren’t. Or are they?
Try this:
  • create an AOI
  • add some local (private) tags. Set them up to be read-only or read/write.
  • create a message as a CIP typed read or write (depending on the tag above).
  • set path to ‘THIS’
  • set the tag name to be the AOI local tag.
  • the destination tag must be of the same type.
  • You may have to format the tag name to be prefixed as program-scoped: “Program:progName.AOInstance.LocalTag”
  • run that message!
  • spoiler: by using the processor’s message router, you bypass the local tag restriction.
- Now try it with tags local to another program on the same controller.
- Then try it on a remote processor altogether.
You can read local tags on a HMI or SCADA as well, provided they're not set to "External Access: None". They're not supposed to be top secret/locked down; "external access" refers only to the ladder logic. You can't address them in routines outside the AOI.
I often display local parameters on HMI's and SCADA, e.g. when displaying a fault code or fault message that has to be stored in a string - you can't set a string as an input or output parameter, and I don't want to use InOut or I have to create an external instance of my string for each instance of my AOI, which kind of defeats the purpose of the AOI.
Right. I discovered recently that building a backing collection (in the form of UDTs) of sets of local tags to the AOI and pulling the UDT tag instead of each individual member is much less costly on comms.
Taking that idea further:
Not directly. With a message, you can.
Yes, you would have to do that, or build a UDT containing AOI + string to 'encapsulate' it slightly better. I'm not particularly focused on strings, but you might be able to tackle that with the approach I'm thinking - external configuration:
In an AOI, for example, I have 'Config' and 'Data' UDTs containing setpoint and actual members like MinFrequency, MaxFrequency, and so on. Even a string member of the Data UDT is certainly possible. An external source, be it HMI, SCADA, separate 'configurator' program on same controller, or a separate 'configurator' controller, would be able to push to these AOIs in single writes with no other knowledge than what the UDT looks like. You wouldn't need In/Out parameters to achieve it.
Yes, that's another approach I've seen used (UDT that contains an AOI instance). I've rarely found an application where that was what I'd consider the neatest solution, but if you have produced/consumed tags in the picture, that could be one of them!
Hi all, hope you are having a great day, I am in need of your help to create a AOI or program that does this kind of job: I have a IO Link...
26
539
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
181
I am very new to Modbus and the industry, so forgive me if I am missing something obvious. I have known Modbus register addresses coming from a...
243
Does anyone know of an AOI using the user ASCII protocol select on the L6x controllers that will talk Modbus RTU using RS-485? Thanks, Trevor...
147
I have an AOI with revision notes. Someone entered the last note into the description instead of the notes. I cannot just click into the revision...
155