The error message on the HMI is:
"Host Communication err
Error Station No:00h"
I am following the IDEC manual:
http://www.idec.com/language/english/AppNotes/ABControlLogixApplicationNotes.pdf
Has anybody had success with this before?
Any help would be greatly appreciated. Thanks!
Correction
Correction:
Allen Bradley 1756-ENBT/A 10/100Mbps Ethernet Bridge (Rev 4.8)
Any help will be greatly appreciated. Thanks in advance
Solution found...but need explanation
I found the solution. Firmware was not an issue. I am unsure why the following worked:
I was using a 7 slot chassis. Originally I had the ethernet card in slot 0, and the Logix Controller in slot 1. I followed the manual step by step and changed the slot numbering when I configured the communication settings. My last attempt was to switch the positions and put the Controller in slot 0 and the ethernet card in slot 1. This worked. I'm not sure why the IDEC HMI needs the controller to be in slot 0. So i tried moving the controller to slot 1 and the ethernet to slot 2. I tried a bunch of other combinations, but the only time it works is when the Controller is in slot 0. Has anybody seen this before? Also, I am wondering what will happen when I have multiple controllers in the same chassis that I want to use.
Please post your ideas!
It looks like IDEC chose the mechanism that would require the least amount of changes from their current DF1 driver; they use the PCCC object and use "PLC/SLC Mapping" so that they treat the ControlLogix like an SLC-5/05 or MicroLogix 1100 controller.
CompactLogix is always Slot 0, and most ControlLogix are installed in Slot 0, and if you send a message to an SLC-5/05 or MicroLogix 1100 to "Slot 0" then the controller will respond, so I'll bet that IDEC took a shortcut and hard-coded the last hop of the CIP path. The user manual you showed does not appear to illustrate a field in the IDEC communications configuration where a Slot number could be entered.
Excellent troubleshooting and investigation on your part !
Hi Everyone, I am currently trying to communicate ControlLogix PLCs via EtherNet/IP with Delta V DCS. There is a VIM2 card configured for...
302
An issue occurred at an organization here in whereby the ControlNet card developed a fault. Card Details: Catalog/Series; 1756-CN2RXT B Part No...
451
Hey all, I'm having this issue with an Allen Bradley AC input card(1756-IA16I). I was looking into another issue and found that the inputs on the...
2,990
PLC is ControlLogix 1756-L73 CPU with firmware 28 In the PLC the value for A60[110] is "AT", Style ASCII, Data Type INT. In KEPServerEX I tried...
1,568
I have a DeltaV DCS system we are putting together and will pull data from a Allen Bradley Control Logix PLC. I am not sure how that communication...
1,140