Can anyone explain to me what Sint,Int,Dint data types represent? or what they mean? I was watching one of the Ab's "How Do I" "Reference a tag in a routine" video and this came up while assigning a bit within a structure?
short answer:
a SINT can store up to 8 bits ... (SINT = "Short integer") ...
an INT can store up to 16 bits ... (INT = "Integer") ...
a DINT can store up to 32 bits ... (DINT = Double Integer) ...
and you didn't ask - but
a BOOL can store 1 bit ... (BOOL = named after George Boole 1815-1864) ...
do you need more information than that? ...
Thanks Ron
And yes I do need more information as I'm now confused as to how I would I assign the data type to a Input of per say a 1769-IQ16. Wouldn't that be a single bit? So where do the data types come in play with that?
in most cases (in fact ALL that I've ever seen) when you "configure" a module in RSLogix5000, the software will AUTOMATICALLY assign the proper data type ...
translation: enter the module in the I/O Configuration - and the software will take care of what data type to assign ...
I get in now the perticulal input would be assign in a INT data type
sorry, but I have no idea what you mean by that ...
going one step further ...
in SOME cases, the software will assign a 32-bit DINT type to an I/O module which only has 16-bits ... don't worry about it ... you'll just use the lowest 16-bits and get on with your life ...
You do not manually create your own tags for I/O data.
That is done automatically for you when you put the I/O module into the configuration.
There are 2 tags created for an Input Module. By example, if I assign an Input Module to Slot 2 in the same chassis as the controller, the tags created are:-
Local:2:I - data Input to the controller from the Input module
Local:2:C - configuration data downloaded to the module
Part of (repeat, part of) the Local:2:I tag that is created, is a 32-bit DINT (called .Data) which contains the data from the I/O points on the module. Yes, it is a 32-bit DINT, so that it can handle a 32-point module, but if it is a 16-bit module, only the first 16-bits in .Data are used.
Simple now...
IN-0 on your Input module appears in the controller database as Local:2:I.Data.0
IN-13 on your Input module appears in the controller database as Local:2:I.Data.13
Hello i have been trying to figure out a good way to take hex and convert it to an array of SINT[]. Here is what my failed attempt looks like.
1,286
I have am programming a Controllogix PLC. I have an Anybus AB7007 Communicator talking Modus RTU to a temperature controller. The tags it is...
16,990
Hello, I am trying to read a barcode scanner input using a cognex dataman 280 barcode reader, store it another string, the compare with another...
62
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
171