I have a CPU 315-2dp plc using for profibus communication with the SEW Movidrive MDX61B inverter.
In the hardware configuration I have fill in the adresses for
communication Input: 264 and Output 264.
When I program example L 1500 T POW 266 in a network and I
download this to the plc the plc are going in stop!
By the diagnostics I see I/O access error.
But I don't know what the fault is.
Profibus communication is working good (led is of on the DFP21B).
Any idea?
Greetings,
mulderm
Hello,
mulderm
Can you monitor the PIW values in a VAT?
Please check that the green LED is on and the red LED is off ?
Are the dip switches set correctly for the profibus interface?
Hello guys,
Yes everything is correct.
I can't also see the PIW in the vat-tabel.
Also changing the address (see attachment) but no result.
What can it be?
Greetings,
mulderm
Hello guys,
What can it be?
Greetings,
mulderm
What about the consistency? If it is by total area, you will have to use DP_READ/DP_WRITE to access the PIW/PQW.
But since you now have moved the IO to the process image area, it should work as JRW says.
Kalle
JRW,
I tried QW and IW but nothings changes!
No values to the inverter!
Vat-tabel is now working well.
DP_READ/DP_WRITE can't used (SFC14 en SFC15)
because the cpu 315-2af03 IS TO OLD.
I don't know sew. I would assume you have to map data out of the drive ?
Can you see any receive data in the drive? Using the drive software?
How is sew drive configured in hw config? i smell need for sfc 14&15.
Yes. You need to use sfc 14&15. PDF shows your config.
For a test
Change your telegram to 2 words of send and receive
From another post of yours I believe your using an old CPU?
Lets test Turbourpo's response
I missed post 8
A 2af03 CPU did use sfc14 and 15
What error are you getting when you use it?
Did you "see" data with 2 words of send and receive ?
merry christmas and happy new year i have a click c0-00dr-d and allen bradley 2711c-t3m. can the panelview talk to the click plc via modbus...
220
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
692
Hi Any one here please helpmein simulation of s7 300 plc program with factory io. how to connect. plcsim 5 doesnot have option of s7 300 ..:
1,011
Hello, I have a bit of a situation, and I think I know the answer but this font of knowledge may prove something. I want to do the unthinkable...
2,175
hello guys, I'm trying to establish a connection between Indusoft 8.0 & simatic Plcsim but I keep getting the following error: error...
1,358