Compact Logix Programming Help
Apr 2013
ms
HI I am a beginner Programmer and am trying to set up a simple line speed reference using a rotary encoder in to a high speed counter on a L24ER QBFC1B and out of analog to a power flex drive does anyone have any sample instruction that could get me started Thanks in advance.
Welcome to the Forum !
The more information you can give, the better the answers you will get.
What you are describing sounds to me like a "velocity follower", where there is an encoder connected to a moving belt or mechanism, and you are trying to get an AC drive to follow that encoder's speed.
The 1769-L24ER-QBFC1B controller, as you have seen, has a 4-channel high-speed counter module embedded in it. It is similar, but not identical, to the 1769-HSC High Speed Counter module.
This isn't a motion axis; it's really meant for taking discrete actions on embedded Outputs based on fast encoder counts coming into the module.
I have not used the L24ER-QBFC1B controller personally, but from what I understand it is most similar to the 1769-HSC. Get the HSC user manual, Publication 1769-UM006, from the RA Literature Library.
Set the counter up as a Ring Counter. For the maximum count, let's go ahead and enter the number of counts your encoder goes through in one revolution.
Then look at the automatically-defined Module Tags created for the module. You'll see a tag like Local:3:I.Ctr0CurrentRate, which should tell you the number of pulses per second you are seeing from the encoder. Detailed information on the Cyclic Rate mode starts on Page 32 of the User Manual.
Thanks guys lot of good info I know there is several different ways of programming this with all types of instruction but is there any one way that's better or easier thanks
The first step is to just do the configuration part; the High-Speed Counter will give you a value for the Rate without having any instructions at all in your program, if you configure it correctly.
The more effort you show, the more help you will get.
I have an Compact Logix L33 communicating with a MT(Metler Toledo) IND131. I need to writ PLC code for dispensing product. I have a hopper that...
1,951
I got a String from the seriell port: "134r200r2r1r250r" I want to put each number into a different DINT-Tag. I did that by a very long Ladder...
4,156
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
101
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
115
I've blown the Output Transistor on the Output Card of a Compact Logix 1769-L24ER-QBFC1B It says J378. Does anyone know the replacement part...
205