RSLogix suppressing minor fault flag after arithmetic overflow
V0N_hydro
Sep 2010
lower mainland
560
I have a counter which is a DINT in both compactlogix and control logix. Sometimes it rolls over, and that is fine. I have logic which does CNTR_delta := CNTR - CNTR_last ; This sometimes generates an arithmetic overflow minor fault, and that is fine.
I do not want this minor fault to be logged when it occurs. I have tried
routine_A: xic S:V OTE overflow_before
routine_B: CNTR_delta := CNTR - CNTR_last;
routine_C: XIO overflow_before OTU S:V
but the minor fault is still logged.
Is there some way to reset S:V, the overflow system bit, or S:minor, the minor fault flag, before it is logged in the controller properties?
I thought that if I reset S:V before the end of the program or task scan it wouldn't end up in the log but clearly that is false.
Thanks for any hints
No, not to my knowledge. Logix platform minor errors are logged at the instant they happen.
If you have the FBD or ST language available, make an FBD routine, and use the PMUL instruction in it to generate your scan delta. It handles rollovers gracefully. I generally use it with the word size set for 8 to 16 bits, and a multiplier of 1.
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
87
Hi folks, in the alarm manager of Rslogix 5000, the tag-based alarm has been created. But when I tried to change the condition, it was found the...
157
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
176
I am completely stuck on building a ladder program that requires a start button to be pressed 3 times to turn on motor 1. Then motor 2 starts...
20
582