Maybe this will clear things up for you.
1/2-slot addressing:
• one half of an I/O module slot = 1 group
• each physical slot in the chassis corresponds to two words (32 bits) in the input image table and two words (32 bits) in the output image table
1-slot addressing:
• one I/O module slot = 1 group
• each physical slot in the chassis corresponds to one word (16 bits) in the input image table and one word (16 bits) in the output image table
2-slot addressing:
• two I/O module slots = 1 group
• each physical 2-slot I/O group corresponds to one word (16 bits) in the input image table and one word (16 bits) in the output image table
If you are using this:
chassis 2-slot addressing 1-slot addressing 1/2-slot addressing
4-slot 1/4 rack 1/2 rack 1 rack
8-slot 1/2 rack 1 rack 2 racks
12-slot 3/4 rack 1 1/2 racks 3 racks
16-slot 1 rack 2 racks 4 racks
Similar Topics
Hi All, I am looking at a future project that includes a PLC5 with some digital I/O. Its been a long time since I have worked on the PLC5...
Replies
4
Views
1,605
Hi all, I am currently working on a project to convert three PLC5's to CLX using the Rockwell migration tools. I was wondering if it were...
Replies
16
Views
9,920
Hi, I need to add two I/O cards to a PLC5 installation. (one 16 bit input and one 16 bit output card) The processor is a 5/40L In RSLogix...
Replies
19
Views
10,614
We have a PLC-5 with 16 I/O Modules in a single chassis. 1-Slot addressing is used with a 8) 16pt-Input and 8) 16pt-Output modules. The I/O...
Replies
4
Views
5,007
I have a DL06 PLC from Automation direct and I am trying to learn how to use the expansions slots in my program. Coming off of allen Bradley...
Replies
20
Views
6,245
Back
Top Bottom