Hi Guys,
For devices that come with 10-32VDC input power supplies, is there any advantage of supplying them with 24VDC versus 12VDC? Does it make a difference, or do you just go with whatever is available on site(voltage wise).
Thank you,
EE
 
24V will mean smaller conductors for any higher current devices.

Loop powered devices have more available voltage at 24V. Driving a typical 250 ohm input impedance at 20mA requires 5V just for dropping across the input. That's only 7V for the device. I've seen many level sensors etc stop operating when the battery voltage drops below 11.5V.
 
As far as I'm concerned, 24V makes more sense, an electronic device that has a range of 10-30V will work on 12V, however, there are a number of factors, running equipment that is designed for those voltages on 12V means you are nearing close to the lower end of it's working range, a drop in voltage from the normal 12V (caused by a number of factors) i.e. noise, voltage drop on cables etc. may cause false triggering. 24V is the most common supply voltage in automation for low voltage systems so there is a relatively a good supply of spares.
 
It is easier to build a small 12vdc solar-powered RTU than a 24vdc one. 1 battery, 1 solar panel. Components that run on 12vdc are preferred for this type of application.
 
In addition to what has been said, a device that can run using 10-32V supply will convert anything beyond 10 V into lost heat. That's more of a theoretical problem than an actual one, but it's there.
 
I vote for 24V

I'm an instrument guy. My 30 years of experience shows that

- the ability of all loop powered instruments to deliver a current signal is dependent upon the available voltage.

- many, many, many instruments would not function at 12Vdc with vendor-supplied dropping resistors on the analog input.

- Substituting a lower value resistor would likely cause HART communications on HART-enabled instruments to fail (HART requires a minimum 250 Ohms loop resistance).

- a significant number of 'instrument' failures over time are due to a failed power supply. Standardizing on a DC power supply is prudent. The VAST majority of automation DC power supplies are 24Vdc. Other voltages are 'different' and not the norm. (re-iterating Parky's comments). 12V is the oddball, 24V is the de facto standard.
 

Similar Topics

Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
23
Views
638
Hello All, After trying to transfer some field changes on the safety scanner microscan3, and verifying, the device is stuck at .... waiting for...
Replies
1
Views
118
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
Replies
1
Views
111
Hello, I'm looking for a dirt cheap digital display + input, that would be wired to an analog input and analog output. This would be for my home...
Replies
10
Views
288
Hello, I am trying to read a barcode scanner input using a cognex dataman 280 barcode reader, store it another string, the compare with another...
Replies
1
Views
117
Back
Top Bottom