Hi guys I have a 1746-NI8 module in slot 1 (4-20 mA selected) that is causing the processor to fault. I did not write down the exact fault but it states Slot 1 fault bit set to 1 in modules diagnostics. I'm using 6 inputs on that module that are all level sensors for waste water tanks. My question, is there any way to find out which channel is causing the fault in the modules diagnostics?
Here is the error message. "Specialty module in slot 1 has generated a generic fault. The card fault bit is set (1) in the module status byte."
After a power cycle the fault clear. But after about 45 min the same fault has been generated. I checked all the junction boxes that the analog wiring comes in to, it all looks good. Now could one of the analog devices generate the fault? or could this be the module itself?
Mickey once the fault is generated the modules Channel status LED's are off, and the Module Status LED is off
Yes I tried to reseat the module and the RTB, after the power cycle the fault cleared, than again after 45 min the fault generated I have a spare module, but I want to make sure that the problem is not coming from the analog signals.
May not be your issue, but might be worth checking the date code on the affected module. We had a few of these that caused us some random pain.
Rockwell Automation Support Center
69003 - 1746-NI8 anomaly - module status LED off
Product Family: 1746-NI8 Analog Input Module SLC
Specific Catalog Numbers affected: 1746-NI8 Series A
Date codes affected: 0202 to 0803 (MMYY)
Hi, having some issues with scalings (SCP commands) with some Vegapuls 65 guided wave radar level transmitters. I've set the min/max in the...
241
Hi everyone, I have a SLC 500 (5/04) with a 1746-NI8 Analog module input. I have two questions: 1. I have noticed there is a IN0-, IN0+ and...
3,544
Hi Folks I am wireing a 1746-NI8 analog card and I suspect the card is bad... unless I am missing something. I have the literature for the module...
1,862
Trying to read analog inputs from 1746-NI8 card, but values show 0 and channel status LEDs never come on. Details: - SLC 5/05, 1747-L551...
2,961
Wondering if anyone has seen this and possibly knows how to fix. We have an SLC 5/05 with an NI8 and an NI4 in slots 1 and 2 in the rack. Both...
3,509