1747-asb
The E50 I/O Parity error on a SLC 1747-ASB module is related to communication issue between an ASB, chassis and the I/O module reported by corresponding slot number (L##).
The main causes are noise, bad I/O module, bad chassis, bad interconnect cable between chassis or bad power supply.
To determine if the noise could be the possible issue remove all terminal blocks from all of the I/O modules and see if the error code persists.
Add each terminal strip back one at a time to determine which module re-introduces the issue back into the system and check those devices wiring.
Otherwise, try to remove each module from the chassis and inspect for damaged termination points. Also inspect the pins on the Modules themselves. If any of the Modules appears to have bent or damaged pins, attempt to straighten them and if necessary, replace the Module
Hope this helps,
- fuzzy logic
I have been asked to add new hardware to an old system. The PLC is a 5/04 SLC. In local rack, slot 25, is a 1747-SN connected to a 1747-ASB in a...
2,512
We are doing a conversion from a PLC 5 to controllogix. There are 4 remote racks in the system. Everything was working perfect until we upgrade...
1,786
hello genious i have one slc cpu and with the slot of 1747-SN scanner module. and it is connected in to 2 slaves by 1747 ASB modules with...
1,992
I have 2 X 17 slot chassis connected with EN2T cards In Chassis 1 there is a 1756-L71 in slot 0 and a DHRIO in slot 1 + other cards The program...
1,516
We had a storm last night, and the smoke got let out of some of our PLC equipment. I'm troubleshooting a link between a 1747-SN and a 1747-ASB...
4,263