1747 dtam
acidflame
Jul 2019
malai
hello i hope you are having great day :oops:
so my problem is, i have a 1747 DTAM-E conected to a DH485 interface
it was working fine.. after some days i turn the ON the machine and the Dtam only showed on the lcd display a blinking dot "." with the status indicator in solid red.. i tryed to pres 7 8 enter at the same time to "Reset" the DTAM but it dosent do a thing even if i press all the buttons it dosent do a thing, only blinking dot and red indicator..
if you guys have any ideas what it can be or what i can do to help me out, because i cant find that error anywhere.
i attached a image of the error.
Thanks.
Welcome to the PLCTalk forum community, and thanks for including the photograph.
Unfortunately, a solid red status LED generally means that the module had failed its internal diagnostics and cannot recover.
The DTAM-E user manual says that you should also check the DC power supply to be sure the module is receiving a sufficient 24V DC supply voltage.
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1747-um004_-en-p.pdf
Thank you again.. i did a test from the cable that is energizing the DTAM and im not reciving 24v DC.im receiving alot less . now i have to dig deeper in the PLC.. there is abig chance that i can fix my problem with that.
thank you
Our SLC500 5/02 had a CPU fault for an unknown reason. The program was gone so I had to re-download the program. And it's running now. But...
3,333
I have a 5/04 SLC hooked up to a 1747 DTAM. Using a link coupler, which from what I gather is DH485. I have some msg instructions in the program...
3,354
I have a old 1747-DTAM I cant find much info about it on the web, Its not a plus or micro or E. Does anyone have a manual for it or know what...
2,564
Hey.. What is the best Substitute of 1747-DTAM (SLC 500 Data Table Access Module)... Suggest plz... what can be replaced with it? either Panel-view ?
2,978
I am trying to connect a 1747-DTAM-E thru a 1761-NET-AIC and then to a 5/04. Based on the DTAM manual you can do this with a 1747-AIC to a...
3,041