And from your reply in that same thread it sounds like you are still having trouble.
The 1747-UIC is very solid. You must follow the directions from Rockwell (directions come with the device) to configure RSLinx. Sometimes I have to reboot my computer but it always works when I follow Rockwell's directions. Do you have another PLC or another computer you could test it with?
The DH485 UIC devices option is not on my ver. 2.42 of RSlinx.
If I download the latest copy (ver. 2.54) from RA website will it be there? (Downloading now)
Why do you recommend this versus the RS-232 DF1 devices?
Thanks
Mickey's correct (again) I have a driver setup for a UIC and it works everytime.... I don't have to change anything, just plug in the cable and start RSLinx then play
Just make sure that you plug the cable first or your will need to stop and restart the driver