1756 Analog INPUT modules
grisu91767
Jan 2012
socal
I have a PLC rack with 5 analog Input modules where I get the max value on Inputs which are not used.:confused: the attached picture shows card #8 where the Input's 3-7 are not connected to anything but show the max engineering unit.
My guess is that the backplane or one of the modules has a power short. Any other suggestions? Help?
I don't have direct experience with this card, but it looks like the unused inputs have floated up to their max value. Try connecting a resistor to ground for each input and see if that doesn't cure the problem. 1K to 10K should work, wattage not important.
The module is just signalling a "wire-off" condition by setting the channel data to the "over-range" value.
Page 66 of the manual explains this, although confusing. The IF16 goes up-scale (+10.25 in the default configuration) for wire-off if using Float Data, and Down-Scale (-32,768) in Integer mode
Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
1,211
Good evening, just a dump question, I’ve configured channel no 13 with scalling as attached, then shown not linear reading, even when i simulate...
1,713
Hello! I am trying to wrap my head around how to wire a 4-20mA sensor to my AB 1756 ControlLogix IF8 Analog Input card. Could someone educate me...
3,828
Hello, I have a flow meter that has been in service for a few years now. I have recently noticed that my registration on the mag meter does not...
1,128
Good Evening , I have a 1756-IF16 Analog Input card already installed in a working ControlLogix Rack. I need to add another Analog 4-20 ma...
2,194