Sorry for the delay, I had started replying you right away but a pesky palletiser was calling me...
I had actually written a paragraph at the end of my last post, but then decided to delete it and keep it simple. It basically said how I reckoned you will now probably come back and tell us that the Enterprise Network is actually accessing this chassis in through the 10.5.55.100 ENBT and not the other way around. I was right.
All of your screenshots and attempted configurations point us in the direction of you trying to configure remote browsing out through the "Automation_Network" ENBT. Not the other way around.
If you place your workstation's IP address on the 10.5... Subnet, and not the 192.168... Subnet, and browse in to the chassis through the ENBT, then you are looking in from the correct direction for what you are trying to achieve here.
But from anywhere, while looking at the chassis, you should be able to configure any of the communications modules for what you need.
It is the "Configure Browse" settings for the EN2T module that you need to configure here, and so yes, it is the 192.168... devices that need to be added to the "Expected Ethernet/IP Addresses" list. When you look to the "Configure Browse" tab for the EN2T module it should be the 192.168.1... Subnet you will see in the "Available IP Addresses" list on the left.
Add all of the node addresses for the devices connected to the EN2T (drives, HMIs, etc.) that you wish to remotely browse. Again, you do not need to add the 192.168.1.1 node address of the EN2T itself because is is transparent to the backplane i.e. to the 10.5.55.100 ENBT module.
In fact, without having added its own node address to the list; when you browse to the Ethernet port of this module, and all visible devices from the list are displayed, there will also be an instance of the module itself displayed under its own Ethernet port.
That will configure the EN2T for remote browsing from
compatible browsers. So that begs the next question...
Prayder said:
...I am trying to get the single module to talk outside of the plc world to my enterprise network...
...What are you using to mine data out of these "machine centers" into SQL?
Prayder said:
...you are saying that I need to add the 192 IP Addresses...then I will be able to "see" the 10.5.55.100 on my enterprise network?
The 10.5.55.100 ENBT module should be directly exposed to any other node within the same Subnet. For instance, if your "Enterprise Network" is represented here by a Server computer, and its node address is 10.5.55.101, then it should be able to "see" at least the ENBT at 10.5.55.100 without any further configuration of the chassis modules.
If you currently cannot "see", as in at least PING 10.5.55.100 from your Enterprise Network, then there is some other networking issue here that also needs to be addressed.
If you can indeed PING 10.5.55.100, but just cannot "see" anything beyond it, then yes, it may just be the "Configure Browse" settings that will sort all of this out for you.
Because we still do not know what you are using software-wise on the Enterprise Network, it is hard to say whether any of the above will be of use to you, or not.
Regards,
George