Hi all,
I have two modules 1769-IF8 within a Compactlogix L32E system.
Installation have been about 3 years ago.
Lately some values on SCADA coming from analogic modules started to be less then values shown on instruments display.
My analogic modules are configured 4-20mA, 10Hz, EngineeringUnits.
First module wired for 4 wires transmitters ( example In2, page 2.21 ) while second module wired for 2 wires transmitters ( example In0 page 2.20)
Instrument shows 5,3mA output, multimeter confirms the value but the analog input reads only 4.4mA. ie 4431 counts
Simulated output for fixed readings
4ma =3521,10mA =6981,12mA = 7628, 20mA = 9290. Again multimeter confirms the output value.
On first module I am using 7 channels, on second 6 channels.
Found faulty channels Ch1,Ch4 and Ch5.
Took the wires from Ch1 to Ch7, configured the channel, everything ok.
Now the question is why on Module 1 I have 3 channels decalibrated from 7?
Could be anything wrong with this type of wiring? 3 from 7 bad seems pretty much in 3 years.
Second module has 6 channels used all OK.
Thank you
Hey guys, Been a while, I have an odd one. Something that should be straightforward. I have a 1769-IF8 module, looking to add an analog, been in...
4,468
my customer has a full 1769-compactlogix rack. they want to remove the two cards in slot 5 and slot 6 and replace them with two new cards. The...
1,589
Hello! I have a project, use the software is studio 5000 v30, the 1769-L30ER compactlogix controller, 1769-LIF8 1769-IQ16 and 1769-OB16 modules...
1,891
Hi folks, The 1769-IF8 has a ChannelStatus Bit, do you use it? From my reading of the manual, this bit is set when the channel has one of many...
2,279
Can a analog card properties settings such as RTS and filter frequency can be changed with CPU in run mode without causing errors or issues...
1,902