Morning all,
I am modulating two different item in this set up.
One will accept an external source 0-5. (Chnl1)
The other is an Eaton DE1 VFD which, I am reading, requires it's own source (0-10v) for modulated control.
Is there a way to get the 10 volt signal thru the analog module?
I have read the analog modules 1769-um002, the I/O modules specifications 1769-td006, and Publication 1769-IN049A-EN-P for reference
and found only this "Voltage outputs (Vout 0+ and Vout 1+) of the 1769-OF2 module are referenced to ANLG COM. Load resistance for a voltage output channel must be equal to or greater than 1K Ω ."
I "assume" this is the input for the Eaton 10v. Could anyone confirm please
PLC L33, module is 16th and fourth from the PA4
Thank you for your time and attention.