I have a weird situation that I have been unable to figure out. I have a 1769-OFC8 card on my Compact system which is running an L33ER processor and randomly I will lose one of the 4-20 ma outputs on the card.
The card only has two devices wired to it; one is a proportional valve and another is a motor speed input card for a remote motor, both are 4-20 ma.
I have checked the clamp settings and they are 4-20ma limits, so that's right. There are no faults on the module or the processor.
Sometimes, seemingly random in fashion, output 0 on the card just stops outputting (verified with a multimeter). Output 1 still works fine during this time (verified with a multimeter). The only way to "fix" it it so either inhibit/un-inhibit the module or power cycle the system.
The program still shows the output value being sent to the card so I know that it's not a logic issue...plus logically the "fix" wouldn't work if it was.
Any ideas why that happens? A weird random back feed to the card from the device or a loose or shorting wire somewhere are the only things I can think of and I checked for that too.
Thanks!
Type-o it is a 1769-OF8C/A!
According to Rockwell since I have nine modules to the right of the PS this can mess with any of them in a random fashion. Their proposed solution is to move the PS one spot or two spots over.
We had a Processor Failure yesterday. Opened a new in the box Processor, and could not get BootP to work with it. After a few hours of trying...
212
I have a 120V relay, 120V DI card and a analog input. I was wanting to know if i could put a 24V DI and well as a 120V DI card on the same plc...
104
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
131
I have a CompactLogix 1769-L31 and need to communicate with it. I only have studio 5000 on my computer. However, when I try to start a new project...
432
I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
287