I have a 1794 IR8 module I just installed on a cooling tower. It a PT100 RTD and I am returning a reading of 998 decimal. I don't know if I need to do some scaling or what??? It is about 25F outside and it is reading the air right now. Any help?????
If you are using as Rem I/O off a SLC, use the SCP instruction (if available w/CPU you're using) or SCL. If a Logix platform, in ladder logic you have to do a CPT instruction. In FBD logic, use the SCL instruction.
Thanks!!!
This is flex I/O off of a PLC5. If I have to scale this myself, what is the range that this card returns to the data table???
The manual is located at:
1794-IR8 Manual
You must setup scaling as degrees C or F or -32768 to 32767 or 0 - 65535. If setup as degrees C, it will read in 0.1 degrees C.
If setup as degrees F, it will read in 0.1 degrees F.
If setup one of the other 2 ways you will need to scale result.
See chapter 4 for configuration/
Kim
Hello everyone. I have installed a remote Flex i/o enclosure with a AENTR ethernet adapter and an 1794-IR8 RTD card. I have landed 4 RtdÂ’s on...
805
Control logix CPU connected to Flex IO via Controlnet The Flex io consists of 5 modules IB10XOB6/A IE8/B IE4XOE2/B IR8 IR8 The 2 IR8 modules...
2,033
Anybody can help me. I already read document in software rslogix 5000 and I think i can use software rslogix 5000 calibrate for flex module...
1,746
Hi there have recently installed some Flex IO to replace some Solartron IMPS and an old style Emerson Scanner. But I am having issues with some...
1,418
HI, I need a help! Recently, I had wired a RTD Pt-100, a=0.000385, range at: -328 to 400'F temp. sensor to the I/O Flex RTD module: 1794-IR8. I...
4,181