maxketcham
Lifetime Supporting Member
If it is 208 then you will want to acquire a 240 to 120v transformer of sufficient KVA. you would hook it between one phase and ground on the 120v side and use the 240 volt side for you 240 v.. that would be a 2:1 transformer. remember you need to know the KVA, not amperage of what you want to supply. A 1Kva transformer will supply approcimately 4 amps at 240 volts using this KVA. if what you want is a 3 phase output it will be different.