6ES7331-7PF11-0AB0 Siemens TC module wiring question
p17061
Sep 2009
Aberham
23
Hello,
We have a project in which we will use the 6ES7331-7PF11-0AB0 TC module for measuring temperature. We use K type thermocouples normally. Our electrician has drawn the system with the K type thermocouples connections in a junction box and then the wiring leaving the junction box to the PLC 6ES7331-7PF11-0AB0 module is normal LIYCY 8x0,34 cable that is not thermocouple cable. He then has the PT100 external compensation thermometer connected in the same junction box and from the junction box to the 6ES7331-7PF11-0AB0 module is normal LIYCY 8x0,34 cable. I am wondering how this will work if the K type thermocouples are connected in the junction box and the wiring back to the module is of different materials than the thermocouple? Is it so that when using a PT100 external compensation thermometer, the channels measure the voltage and it does not matter that the wires connected to the module are of different materials than the thermocouples? We will use "external compensation" in the module configuration.
Thanks for your help!
Pete
It is in the junction box where you will be creating "Cold-Junctions", i.e. junctions between your "K" thermocouple metals, and your copper wires.
These dissimilar metal junctions will generate their own voltages, which must be accounted for to get a proper reading of the "Hot" junction, i.e. the thermocouple itself.
Mounting the PT100 sensor in the junction box is exactly the way to compensate for the thermocouple effects of the connections in it.
I have never had the pleasure of working with a "Thermistor" until now and have a question. The Thermistor is a 10KOhm 4-20mA 2-wire device and I...
138
Hi All I am using 2 x analog cards on my rack and they are described as 12bit cards in there title. The manual suggests that the resolution can...
2,053
Dear sir, I am using SIMATIC 300, CPU 315-2DP , (6ES7 315-2AF03-0AB0) VIPA 603-1CC21 A1.0 RAM 32KB, Firmware=V4.0.8 The problem Im using MPI...
203
Hi , we try to get a CPU 317T-2 D back to life,memory card was defective and with some resets we have only sf light red flickering we...
28
789
Dear All I am currently trying to configure my S7-1500 CPU to read a 4-20mA value at channel 1 Analog Input Card Module (6ES7531-7KF00-0AB0) 4...
2,893