AB 1746-BAS Module not starting in RUN mode
JerryH
Mar 2009
Tellico Plains,TN
110
I am trying to run a program out of RAM but each time power is applied the module starts back up in command mode. I have pulled the EPROM chip to try to force it to RAM but it has no effect. According to the manual it should startup in RAM if a program is present.
What is keeping this module in command mode?
thanks
Jerry
Make sure you have the following manual from Allen Bradley
1746-RM001A-US-P
Read the command PROG, then the command PROG2
These tell you how to transfer the RAM program to the EEPROM (PROG). Then you command the module to start up in the RUN mode (PROG2). Make sure you have your communication jumpers set. Decide whether you want a CTRL-C from the command port to be able to stop the program.
We use this module so infrequently that I have to get out the manual each time and refresh my memory on these subjects.
You need manual 1746-UM004B-EN-P. Look at the jumper settings for JW4. The factory default config powers up to command mode, but you can set the jumper to run the program in RAM.
You got it. The manual has a side note I didn't catch that explains when the program port starts up with default comm settings it also starts up in command mode.
I had to change the jumper to select the program port to startup with programmed comm settings and it will also start in run mode.
thanks,
Jerry
Hello, We have an older SLC500 controlled system that is using a BASIC module to communicate to a third party device. Looking into converting the...
1,284
Hi, I am upgrading a AB PLc to Siemens PLC logic and everything is ready for siemens but the problem is the existing PLC is communicating to DCS...
4,779
I'll admit that in all these years I have only encountered M0/M1 files one other time, and it was used to communicate with Eurodrives. In a SLC...
1,739
Hi all, We have a old machine with SLC control system, which communicates with barcode scanner through 1746-BAS module. And it works very well for...
1,581
Please I need to know how to add an image into a paper label, Im using a 1746-BAS module to send the data to a printer. thanks
1,830