I'm using an L33 PLC with an Ethernet I/P Point IO 1734-VHSC24 high speed counter to read in from an encoder, then calculating the counts per cycle. I've been having issues where the PLC cycle time is much faster than the IO update rate, such that in practice, I get several PLC cycles with the same count value, then a jump next time the IO updates.
I see that I can reduce the interval at which the IO updates, but I'd prefer to somehow link it's update to a timed task, or to the logic that reads in the counts, such that the count value is always up to date. Is this possible please?
Create a tag that contains the "last value" of the counter and then compare it to the current value. If they are not equal set a bit enabling your logic. At the end of your logic, copy the current value to the last value.
** keep the scan times as originally set, don't change them
since this is a CompactLogix platform - you might need to consider this ... it's a long shot - but it MIGHT be your issue ...
QUESTION - how many Tasks are you using - and what do you have their Priorities set for? ...
reason for asking: the CompactLogix platform (but not the ControlLogix) uses an "I/O Task" which has a priority of SIX ... so ... if you have other tasks with higher priorities (lower number settings) than SIX then SOMETIMES the Input and Output signals get "lost in the shuffle" when high-speed operations are involved ...
DISCLAIMER: I know that this can be a problem with Version 16 systems - but I have NOT had a chance to explore the same issues with higher versions ...
why not put the calculation in periodic task sub program
You will find that there are may thinks the normal scan time is to fast and you have to put them in a periodic task program PID is one of them
is it possible to external read the Forced_value list from a PLC using UnityPRO? I need to get this data. It could be via modbus, ops... or even...
2,444
So View SE 10 was the last to support HMI alarm tags. View SE 11 says you must migrate them to Alarm and Events. The View SE alarm summary will...
1,894
So I have a dryer project that connects to the PLC and says "equal". When I connect it shows there are forced bits, but when I double-click on the...
2,185
Hello All, I am using Allen Bradley Control Logix system, from the machine supplier I got the controller program developed in RS Logix 5000...
2,033
Hello PLC gurus... I have a very basic question. If I have forced values in a PLC and I cycle power to the PLC will I erase or retain those...
1,970