AB PF755 Drive can not view Online in Studio 5000

Nan

Member
Join Date
Jul 2015
Location
louisville
Posts
126
Hi All, I am having an odd issue, need help now!:cry::cry::cry:

The studio version is 32.13, drive add on is 5.08.

PLC is l36erms, the 755 drive is standard + safety, it was working until I change processor IP address.

After I change PLC ip address, there is yellow mark on the drive under device tree, I think it was caused by the ownership, it has to be reset.

However, when i trying to reset the ownership, right click the drive-property, the property page opens, then the mouse is just keep circling, it frezzed.

What do I need to do? Sould I recreate the 755 in the project or reset the 755 to factory default? How should I reset to factory default?

Thank you!
 
Did you upgrade the firmware in the plc recently? Plc version 32 to PF755 version 5 is a very wide margin. Off the shelf PF 755 is up to version 14 at least, possibly 15.
 
Did you upgrade the firmware in the plc recently? Plc version 32 to PF755 version 5 is a very wide margin. Off the shelf PF 755 is up to version 14 at least, possibly 15.

PF 755 is 14 004, I did not upgrade plc fireware. Ever since I use version 32, studio slow down quit bit.

I talked to AB suppot today, they asked me to upgrade drive add on to 5.08(Released today), still does not fix it.

At this point, I really hate AB software.
 
For those of your who may have the same issue, export your project to L5K, import again, if that does not work, inhabit the PF755 module, upload, go online, should work. If still does not work, starts with a new project, this problem is caused by different user go online with differernt version AOP, or software glich.
 

Similar Topics

Hello guys, how are you? I´m trying to conect a PowerFlex drive 753 with a 1203-SSS cable, but I get some errors with RSlinx Classic. I add a...
Replies
3
Views
1,796
PF755 & compactlogix; Control 8 drives at the same time. somt. a drive wil not move Controlling 8 drives at the same time. Sometimes 1 drive will...
Replies
6
Views
3,656
Hi, I am having issues matching a 50HP submersible pump w/ a PF755 VFD (480V 3-Phase, 65(ND)/52(HD)). The failures occur at the static...
Replies
7
Views
989
I have a relatively small network but I am having some issues with PowerFlex 755 drives (using the native ethernet card) Faulting with the F926...
Replies
0
Views
218
I am having some trouble understanding what the break frequency is on a pf755. This is set in parameter 63. Rockwells description reads like the...
Replies
1
Views
791
Back
Top Bottom