I've a DH+ network connecting more than 20 AB PLC-5. I use the usb to DH+ converter (1784-U2DHP) to monitor and troubleshoot problems. when the DH+ cable is pluged in to the network the Rslinks does not see any of the PLCs on the network however the network for the m/cs is healthy and all m/cs are running. only when I disconnect the network from the PLC that I'm pluged in to, only then the RSlinks can see that one PLC and communicate withno problems. I've changed the lead, PC and I've tried to plug in to another PLC and the result is the same. Can any one help please? Thanks
 
I've a DH+ network connecting more than 20 AB PLC-5. I use the usb to DH+ converter (1784-U2DHP) to monitor and troubleshoot problems. when the DH+ cable is pluged in to the network the Rslinks does not see any of the PLCs on the network however the network for the m/cs is healthy and all m/cs are running. only when I disconnect the network from the PLC that I'm pluged in to, only then the RSlinks can see that one PLC and communicate withno problems. I've changed the lead, PC and I've tried to plug in to another PLC and the result is the same. Can any one help please? Thanks

Perhaps the node # of your RSlinx DH+ converter is the same as an existing node on the network.
 
What do the status indicators on the USB device tell you? See PDF below.

I would try a very high node address e.g. 63. It can't hurt.
 
What do the status indicators on the USB device tell you? See PDF below.

I would try a very high node address e.g. 63. It can't hurt.
Thank you,
I found the problem. There was short in the wiring of the DH+ network. What makes me confused that the netwotk was healthy and all machines were running and communicating with each other with the present of the short in wiring !!!
 
Thanks for coming back with your solution. Good to hear all is well now.

The addition of one more node may have tipped the network over the edge.
 

Similar Topics

Hello, I want to connect the Factorytalkview ME with rslogix500 to see the live response of HMI buttons in Rslogix500 ladder code . I am using PLC...
Replies
4
Views
38
I have a cell with a compact guardlogix as the plc and I have three hmi's and two vfd's on this cell. I been experiencing momentary comms faults...
Replies
10
Views
86
Hi, hope you doing well I am looking for SIEMENS PLCSIM equivalent in GE FANUC PLC, RX3i PLC thank you
Replies
2
Views
30
Hai, I'm working on Allen Bradely PLC RS Logix 5000 V20 i tried to communicate modbus communication with AB plc and RS 232 to Ethernet converter...
Replies
1
Views
55
Trying to learn PLCs going to start by buying an Arduino Opta Wifi to practice with but what's the PLC I should get next?
Replies
10
Views
255
Back
Top Bottom