AB PLC5 Integer Maximum Elements Allowed
GENERY
Feb 2011
Singapore
Good morning. I have a question regarding AB PLC5.
We have a AB PLC5 Processor (1785-L40E Rev B) in our plant with an existing running program on a running machine. I uploaded the current program and tried to download it to another AB PLC5 Processor (1785-L40E Rev D). But the downloading is unsuccessful. The error shows that N7 Integer file elements is more than 1000. Indeed I checked the uploaded program, the N7 Integer file elements is 1029.
I tried to change the N7 Integer file elements to 1000 as maximum on the uploaded program and it is able to download successfully. Then tried to go to program mode and changed the N7 Integer data element to 1029 but it won't allow me to do so.
I wonder how the existing running AB PLC5 (1785-L40E Rev B)processor was able to accept the existing N7 Integer File with 1029 elements. šŸ™ƒ
What is the maximum allowable Integer file elements for a 1785-L40E Rev D processor? Is there any other way to configure the N7 Integer file of more 1000 elements that can be downloaded to a AB PLC5 Processor?šŸ¤žšŸ»
PLC-5 controllers have both a Series Letter and a Revision Letter.
The Series letter typically determines the physical hardware and the general capabilities of the controller. The Revision letter (sometimes a letter and a number, like "N.1") is only a firmware designation.
The PLC-5 controller operating system changed the limit on data elements per data file from 1000 to 2000 with the introduction of the Series E controller.
Thanks for the reply Ken. I forgot to mentioned that both the PLC5 processors that we have right now are Series E processors. Only the revisions are different.
While in offline mode, I can change the N7 integer file number of elements to more than 1000 elements but it does not successfully download to the 1785-L40E Series E controller.
There is a pop window showing the following details.
Download Failed!
Created Section Failed:Ext Sts - 0X01
Illegal Address
section=Data, file=7, length=1029
From my understanding this refers to data N7 Integer file which is currently configured with 1029 elements. Thus, when I changed it to 1000 elements then downloading will be fine without any error.
Memory size should also not an issue. There is still around 23K free memory out 49K memory for this processor.
Does your controller properties screen look like this?
Are you sure you have a series E Rev D controller?
Can you post the .RSP file you are trying to download?
Thanks for posting the specifics of that error message.
That suggests that it's the PLC-5 itself that is rejecting a data table definition being sent to it by RSLogix 5.
I've never heard of a Series E controller failing to support the expanded Series E data tables, but I suppose it's possible that there is a bug.
It's also possible that the controller isn't really running the firmware that's on the label, like if it was remanufactured and the wrong case or label was put on it (by RA or by somebody else). The Controller Properties window illustrated by Mickey in RSLogix or the RSLinx (right-click in the browse, select controller properties) should show you the exact firmware running in the controller.
It is almost the same as the image you posted except for the revision. It is showing B.
I got confused with Revision and F/W Revision.
My PLC processor details are as follows based on the sticker label at the side of the processor:
1785-L40E
Series E
F/W Revision B
Revision D01 (this is at the upper right corner of the sticker)
I am sorry, my company policy does not allow me to share the PLC program. If this hinders you to help me further, it is ok. Appreciate the replies and time you spent on this.
I don't have your controller, but when I try to change the element length to 1029 on a Rev B controller it will not let me, using RSLogix5. However it will with a Rev D.
I am not the expert when it comes to Rev's, but it appears that may be your problem.
Hopefully Ken checks back in.
I found the most detailed PLC-5 Release Notes knowledgebase document from this era (1997-1999). It's in the Knowledgebase, article 18946 (Access Level: Everyone).
Genery's experience is suggesting that a Series E Revision B controller supports data files over 1000 words, while a Series E Revision D controller does not.
That's not backed up by the release notes. Support for 2000 program files and 2000 data file elements was a major part of the first release of the Series E controller in 1997.
The only exceptions I read are a number of the less popular models that didn't get 2000 program file support until Series E Rev E. These were the PLC-5-11,26,30,86 controllers.
In 1999, the PLC-5/40E was by far the most popular model of PLC-5 controller.
It's possible there's a bug or difference that I'm not aware of or that's not documented in that list. I think only Rockwell Automation is going to be able to answer this question effectively.
Hello, I am converting to iFIX 6.1 and talking to a PLC5. I have several TX tags that were looking at N32 addresses in the PLC5 and were getting...
2,950
Hi Friends! How many words are in an Integer in PLC5/04 Processor? In an INTEGER Say N10:0, N10:1, N10:2, N10:3..........N10:x WHAT IS THE...
1,937
Hello! I have a question that I can't seem to find a solution to here on the forums. I am working on an evaporator system where there are several...
8,596
I have noticed in one of our PLC5 programs there is a copy instruction that copies a integer into a floating file. The integer value being copied...
17
9,175
Hi Fella's, GOt a problem with a PLC5, I have an integer number....lets say 1234 for example, and I need to convert this to a HEX number and...
2,770