AB RIO Again
Jezz
Dec 2002
Kendal
399
Hi All,
I'm still having problems with my RIO instillation I'm using a AB 1747-SN scanner to talk to a AB 1771-ASB Series E adapter the fault I'm getting is that the Active and Adapter fault lights are flashing in unison the book says this is a Incorrect Starting I/O Group number and that I need to set the dip switches according to the table (I've done this and no change).
The rack I'm using is an old PLC2 rack(AB1771-A4)it has some 32 point I/O in it but I've set the Adapter to be ok with this and now I'm running out of ideas Help please this is driving me crazy banghead
Big Thanks Jezz
I think there was a thread posted here about those old racks a few weeks ago. It seems that there was an issue between series a and series b racks. I think the a's won't work with 16 point i/o but the b's will. Check with AB and your specific rack catalog #. Doesn't sound like your problem exactly, but you never know with the old stuff.
Were you using 32 point cards with the PLC 2 ????
Do the rack dip starting rack/group match the 1747-sn config???
If it's really a "1771-A4" chassis, it is only going to support 8-point I/O modules, no matter what kind of adapter you put into it.
You're going to need a 1771-A4B chassis (in production since 1985 !).
There is an A-B technote, # A16647, that goes over all the technical considerations when re-using PLC-2 hardware with newer controllers.
Okay, it's time to get dirty with the DIP switches.
Post the DIP switch settings you have for the 1771-A4B chassis, the 1771-ASB/E adapter, and the settings you've made in RSLogix 500 advanced I/O configuration for the G-file of the 1747-SN, which sets up the various I/O addresses you want the scanner to scan.
Here You go Ken
Right the Chassis first
It contains
6 * 32 point DC input cards 1771-IBN
5 * 32 point DC output cards 1771-OBN
3 * 16 point 110v ac output cards 1771-OAD
In These positions
slots 1 to 6 are 32 point Inputs
Slot 7 is 32 point output
Slot 8 is empty
Slot 9 to 12 are 32 point outputs
slots 13 to 15 are 16 point outputs
1 - Off
2 - On
3 - Off
4 - Off
5 - Off
6 - On
7 - Off
8 - Off
The 1771-ASB series E Adapter
S1
1 - 0n
2 - On
3 - 0n
4 - On
5 - 0n
6 - On
7 - 0n
8 - On
S2
1 - On
2 - Off
3 - Off
4 - Off
5 - Off
6 - Off
RIO Scanner 1747-SN
Dip Switches set to 57.6K Baud
Advanced config
Max Input words:32
Max Output words:32
Scanned Input Words : 32
Scanned Output Words :32
Interrupt service routine:0
M0 Length :3300
M1 Lenght :3300
G File Length :3
G file Data
Group 0 in each Logical Rack set to Full Rack Giving me I/O Words0 to 31
Thanks Jezz
Found the problem had the chassis dip switches inverted on when they should have been off and off when they should have been on..
Just a few bug in the software to sort now ..
[rainbow]Thanks to every one who offered help over the past few weeks it's made my life a lot easer.....[/rainbow]
:D :D :D :D :D :D :D :D :D :D
It seems I remember something confusing about the dip switch markings on that adaptor module, I'm not sure what it was, but it was easy to get them backwards.
hello, I have a problem with my AN-X2-AB-DHRIO Prosoft module, I can't connect with the module because I lost a microSD card that has firmware and...
390
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
419
Does anyone have information or documentation regarding the protocol used in Rockwell's Remote IO, and how the physical layer of the network...
938
I have never understood how the I/O is configured using RIO. In the tree there is only the RIO module, not the racks of I/O attached or all the...
1,300
HI All, I would like to know your opinion about the disposition over the 1734 and 1718 rack for the I/O Cards. - Normally I use for the first...
480