AB VFD Fault
barcenjim
Aug 2014
California
We keep getting a Fault on a Allen Bradley VFD "316 NODE FAULT ERROR" can someone give us some help on this what is causing this error and how can we fix tis.
http://pdfstream.manualsonline.com/c/c058fb71-22d6-49ed-b558-7ff5cf3cacaa.pdf
316 206 Node Fault Error - See VFD Fault Code 15
15 206 Load Loss
If this fault appears, there may be a problem with software configuration.
To reset the processor, cycle power to chiller, check ICVC VFD_CONF settings and save settings when exiting VFD_CONF screen. Check VFD parameters with Drive Explorer.
This may help you out.
Regards,
Hi & Welcome to the Forum!
Can you tell us what is the full catalog number of the "Allen Bradley VFD"?
If it happens to be a PowerFlex 755...
This error may be due to poor Ethernet media or poorly seated Ethernet media in one or more Ethernet ports within an integrated CIP network, or it could be more complicated...
516414 - PowerFlex 755 HIM displays Fault 316 Node Fault Error
Access Level: Everyone
Regards,
George
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
286
I am getting a motor stalled fault on a VFD for a incline conveyor motor with a electric brake. I notice that when the VFD is supposed to ramp...
4,263
Hello everyone, We are using a Powerflex 753 VFD to control a motor which lifts and descends loads. The drive goes into fault code 12 (HW...
8,342
Iam getting Fault F021 ("System Fault Current Measurement is out of range"),Any help ??
3,008
I am having some issue with two vfds installed at the same location. They are tripping out on overvoltage faults very randomly. I checked the...
21
5,902