ABB Active analog problem
Aburke
Jul 2008
melb
I am currently working on a job where i am recieving a 4-20ma signal from a tempreature controller. the signal is steady but the value in the plc is jumping around 10-15%
Processors tried, PM554 eco & pm573-eth
analog modules , AI561 & AX522
its only a problem with external sources, loop powered are ok.
i have tried everything i can think of!
I have used "statistic_real" to average it but its not ideal.
hooked the wires up to a SLC plc & was spot on so problem is back in the plc
its on both current & voltage inputs.
I have been using these plcs for around 4 years now & have only just stumbled across this issue.
Thanks in advance
My immediate reaction, too, was use an isolator, so I'm missing something.
a) Does this mean that analog signal is steady when measured with a milliammeter, but the converted data values jump around?
>tried that (isolator?), not a noise problem.
>even with a calibrator it (the signal) jumps around
Let's confirm:
b) Loop powered current inputs do not jump around?
c) But a battery powered, "floating" calibrator the signal jumps around?
d) you've actually tried an isolator and it did not solve the problem?
further info:
d) Is the 24Vdc power supply used for supplying power to loop-powered instruments grounded one side or floating?
quote=danw;484693
>the signal is steady but the value in the plc is jumping around 10-15% Correct
a) Does this mean that analog signal is steady when measured with a milliammeter, but the converted data values jump around? Correct, we put a jumo logger in series & the 4-20 was steady. when the 2 wires are taken off the ABB & put on an allen bradely it is stable
>its only a problem with external sources, loop powered are ok.loop powered is perfect, thats what i have always used in the past
>even with a calibrator it (the signal) jumps around yep, both volatge & current
Let's confirm:
b) Loop powered current inputs do not jump around?no
c) But a battery powered, "floating" calibrator the signal jumps around?yes as does the feed back from the retransmission on temp controller
d) you've actually tried an isolator and it did not solve the problem?tried a phoenix contact 75hz isolator & also a current to voltage convertor. same problem.
further info:
yes, i have used 3 diffent power supplies, 4 different processors (all ABB) and 2 different analog modules
still doing it.....
bugger!šŸ™ƒ
I don't know what a Phoenix Contact 75Hz module does, but the isolator Bryan recommends:
has a loop powered output like your other loop powered field devices so that it should work.
It isn't clear whether other loop powered devices are working with this particular rack/CPU/PS/AI combination or whether this is just a problem with the temp controller re-transmit.
If other loop powered devices are working OK, then using an isolator whose output is loop powered should work too.
But, if a battery powered calibrator is noisy, then that could be a sign that something else is amiss. I am stumped as to why a battery powered calibrator on the same AI card as loop powered devices is noisy when loop powered devices are not noisy.
It isn't clear whether one side of your DC power supply output is grounded (earthed) or not.
Hi, yeah might give that style a go!
Yes the 0v is earthed, also try joining all 0vs together.
Waiting on Abb to get back to me
We have another job which has 87 of these.... Already bought the components too
as you say yourself it is a problem with external, so do you connect the null of the power supply to the i- input and also to the ZP output of the abb.
in abb it is not allowed to have a external power source, so take the VP output for your sensors.
The sensor is an Ex I device so is going through a barrier. On the wiring diagram external voltage / current is ok
does anyone have an install or know if/where i can download it for the following "ABB PS501 Control Builder Plus V2.3 " the software was a free...
90
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
147
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem Iā€™m experiencing is a ABB drive supply a large...
211
Hello all, I have an ABB PLC (PM573) and it has without MC card. I need to take backup from PLC to PC (in automation builder v2.7 ). My...
448
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
185