Active Alarm Issue on Proficy Project
nmb550
Jan 2017
Toledo
I have recently transitioned from a role as a Maintenance Supervisor to a new role as Maintenance Controls Engineer.
I have recently encountered an issue with an HMI not displaying active alarms. Further investigation revealed two HMI in the system and neither display active alarms.
Currently using a QPView 12" TFT (IC754VSL12CTD) and a QPView 6" TFT (IC754VSL06CTD) with a GE Fanuc 90-30 processor, GE TCPIP drivers. Project created in Proficy V6.0 Sim 24 Build 5005.
Project was sent to GE support and verified as a good project and alarm functionality is normal.
I suspect a communication issue/driver issue but am not sure. All other functionality of the HMI appears to be in working order. Alarm bits show active in PLC program.
Any feedback would be appreciated.
A few relevant questions:
Did they display at one time?
Do other variables display? If yes the problem is not in the Comms link.
How are they supposed to display? In an "Alarm window"? If yes verify that it is setup properly, see online help in PME.
Are all alarm variables properly parameterized to be displayed on an HMI, see online help for details.
Do yourself a big favor by updating to the latest version of PME, AFAIK, version 9.0 is still shipping which means that you are more than three years behind. Trust me in PME newer is almost always better.
I was actually able to correct the issue by deleting all of the fxRuntime files from the HMI in both SRAM and Programs folders. This has been referred to as "QPView cleanup". I did, however, discover an error in the project with the Root Alarm Groups and ViewScript alarm filter on the active alarms panel. I was able to connect and download the project without further issues.
I was looking for this function, so that i doesn´t need to do it in the PLC. If there are an alarm in the alarm list, i want to flash the...
555
I'm using FactoryTalk ME version 13. I have an alarm banner that is an on top display. Whenever there is an alarm this banner becomes visible to...
924
Hi everyone! I have Panelview plus that is attached to a compactlogix controller, and I would like to use the built in alarms feature in view...
3,720
Hey All, Is there a way where I can click on an alarm in "Alarm Viewer Ctrl" or any other alarm control and get info back? For example, I have...
3,922
Is it possible to clear an alarm when it becomes active? I have a data tag setup to alarm on Active Off. This in turn sends out an email stating...
2,111