Hi all,
I can't figure out few of addresses in HMI connected to Unidrive SP with RED lion G306 that I inherited. They communicate via modbus, and most of the addressing is for example 401909 meaning 4 - for holding registers, menu 19.09. But i have a few that read 418405. Now 4 is still for holding registers. But other digits don't make sense, there is no menu 84.05 (what's 1 for then?), there is 18.40 but that is only a bit, and what is 5 for then, and HMI reads long word from this address.
I can't match them to any address in the drive.
Any ideas?
Thanx all!!!
do you have any modules installed in the Drive?
It may be option module 1 then an internal address
Unidrive SP Advanced Users Guide
- Serial Communications Protocol
- CT Modbus RTU Specification
- Extended data Types
It is setting INT32 type reads.
To interpret your address of 18405 subtract 16384 ( '01' in top 2 bits ). This leaves 2021 - menu 20 item 20 (or possibly 21 - I'm not sure)
Hi Bernie, you are right, it is for 32 bit reads. I had a look at that part of the manual, but I still can't see the connection between described formats and my addressing of 418405. Would you care to point it out if you know?
I don't know where they got X value in the example not that number 16384!
Thanx!!!
The added on number for extended addressing is the top 2 bits , 00 being the standard types, 01 being 32 bit INT addressing ...
'01' in the top two bits is 16384. So, to convert a standard menu/item address to this for is done by adding 16384.
So, does menu 20 - item 20 mean anything to you? Does it make sense given what the Red Lion is showing in this item?
(All I know is what I read in the manual, I've never used this, but it looks right.)
Ahhh OK got it now. Makes sense. Yes, 20.20 is part of the menu for the drive.
Altough I always get 1 valus smaller when calculating than what is addressed in the HMI. Driver in HMI probably takes care of the -1 part of equation formula described in the manual.
Many thanks for the help!!!
Now I need to get them communicating again 🤞🏻🤞🏻🤞🏻
To make a long story short I am in the process of upgrading a PLC5/40C to a 1756-L81ES. I will be installing a 1756-CNB module. This processor...
4,559
Hello All: I have a situation where I have 110 PID loops. For the most part they are all tuned the same but there are always a couple that need...
5,727
Hi i am converting plc5 program to control logix 5000 can any one suggest me how to do address output module .as we use bits in plc5 and words in...
5,945
I have an existing SLC system that we are planning on putting a new CLX processor on top of. My question is how to address the following SLC IO...
6,728
I'm have been tasked with re-engineering the Error logic footprint of our machine Ladder program. I have the following issues to consider: 1.)...
8,053