I had read this thread this morning and was starting to reply before Ken had when my Son arrived in with a possibly broken finger from playing football. So I've spent my whole Sunday in A&E in the chronically bad waiting system just to get the all clear on the x-ray. Thank God. Swollen, bruised and badly sprained, but he'll survive!
Ye have been busy since I left this morning, but my head hurts a little reading through all the options! Maybe I'm just drained?
I just wanted to reaffirm your options for connecting to both devices from your computer after you have them setup and talking to each other.
As you are aware by now, you do not have the 1747-PIC/AIC+ driver available to you in Windows 7. So once you have the ML1400 & PV550 communicating with the DH-485 protocol via the AIC+, you cannot connect directly from your computer to the other AIC+ port and establish a connection.
If you need to communicate with the PV550, via the AIC+, then you must use a 1747-UIC from your computer and use the DH485 devices driver. The UIC, as you may be aware, is both a USB to Serial adapter and DF1 to DH-485 converter. It would connect from one of your computer's USB ports to either of the serial ports on the AIC+, depending on which one is left free.
This would of course establish DH-485 communications with both devices; which is what I think you'd ideally prefer here?
If needs be, the UIC can also be connected to both devices directly without the AIC+ as it has two available DH-485 ports - RS-232 9-pin & RS-485 RJ-45. However, only one is usable at any one time.
The other options for communicating directly with just the ML1400 is of course using its other serial port configured for DF1 and either a 1747-CP3 or a 1761-CBL-PM02 cable to your computer's serial port; or using the Ethernet port.
But neither of those options will give you access to the PV550 which is connected via the other port. The MicroLogix controllers do not support channel to channel pass-thru or bridging like the SLC do.
If you are working with Allen Bradley equipment, using the DH-485 protocol, then I would always recommend users to have a 1747-UIC to hand.