Allen Bradley 1769-IF4 Analog Input (Calibration/Accuracy Question))
agrajag42
Dec 2015
Bahstahn
17
Hi, I'm using an Allen Bradley 1769-IF4 Analog input crd with a Compact Logix L33ER. Its 14 bit (0-16384), and I'm taking raw readings. I am applying and measuring (with a multi-meter) a precise voltage of 1.50 volts across the analog input terminals. I'm configured for a single ended input signal, 0 to 10V.
The input value I am getting is 2350 which equals 10* 2350/16384 = 1.43 Volts.
The card specs say that it is internally calibrated yet this error is approximately 4.7%, way outside the specs for the card (0.2%). I am not observing any steady state offset or noise on the signal.
I know I can apply a fudge calibration factor in PLC code, but am curious if anyone else has used this card and achieved better accuracy, and what procedure they were using.
Thank you
.... just thinking out loud ...
My assumption is that 0-16384 corresponds to [0 to 10 V] (nominal operating range), not to [-0.5 to 10.5] (full scale range)?
That is what the book says (0 to 16383 = 0.0 to 10.0 vdc).
We use these cards with 4-20mA inputs and I often see a little bit of deviation from the manual... maybe five to ten counts, not 150.
In any case, for our purposes, we do a two point scaling of the raw into engineering units. I don't call it a calibration, just a scaling to real world conditions.
Apply full scale voltage to the input and see what you get.
The other thing that I am curious about... What is your precise 1.5 volts source? Are you measuring it at the same time? If so, the 2nd meter (counting your PLC input point as the first) perhaps has low enough impedance to affect the 1st.
Something I remembered from my circuits class was:
"Every meter impacts the circuit it is measuring to some extent, just as any tire-pressure gauge changes the measured tire pressure slightly as some air is let out to operate the gauge. While some impact is inevitable, it can be minimized through good meter design.
Since voltmeters are always connected in parallel with the component or components under test, any current through the voltmeter will contribute to the overall current in the tested circuit, potentially affecting the voltage being measured. A perfect voltmeter has infinite resistance, so that it draws no current from the circuit under test. However, perfect voltmeters only exist in the pages of textbooks, not in real life!"
I pulled this from this website for reference:
http://www.allaboutcircuits.com/textbook/direct-current/chpt-8/voltmeter-impact-measured-circuit/
I have a 1769-L24ER-BB1B and I am trying to flash it to 34xx, its flashing red and faulted, when I try to flash it I get a popup stating it needs...
273
Hi, i want the above to control a 4-20mA valve using the 20mA signal to open the valve fully and a lower signal to partially open the valve how do...
2,567
Hi Guys, Question - does the subject title AB processor act as a processor AND comms module? It does have communications ports available on the...
972
Hello everyone, I am in the beta phase of building a SCADA system. Currently planning to use Inductive Automation as our SCADA platform, but...
2,153
hi, this is my first post in this forum, i have two allen bradley 1769-L30ER and unfortunately I want to make it redundancy. but I heard that...
3,046