Allen Bradley Micro 850 analog ouput
NoName
Sep 2003
Domžale
273
Hello all.
I'm working with an Allen Bradley micro 850 PLC.
I am configuring an analog output module to give me 0-10 V value to another PLC's input.
I scaled a percentage value from the process of the AB PLC to integers with a max value of 29647. So 100% is 29647 (integer), but the actual voltage is not correct.
I have 40.6 % value of the process, so the output volts should be around 4V, but they are 7 volts.
I configured the analog output module like so:
Mimimum-Maximum output range: 0V to 10V
Data format: Raw/Proportional data
Can any one please help me how to solve this.
Cheers Aliex
Your rung (I'm using ladder function blocks) should look something like this.
You have to convert the (Analog Input)RAW WORD into a real before you scale it, then you convert the outcome back to a WORD and mov that value in the Analog output (_IO_EM_AO_0).
Hello.
Thanks for the input guys. I sorted it out based on the reply I got from AustralIan. See the attached picture of the LAD logic.
Again thanks for the help.
Cheers.
Aleix
This unit was removed from one project where it had perfomed nicely. Wired into simulator and we have no signs of life no LED,s lit power...
948
Hello Everyone, Hope you all are doing well. I am new to the PLC and communication protocols used in PLC. I am currently stuck with Allen...
47
13,889
Hi all, I have problem that I could do with some help with: I have a setup consisting of an Allen Bradley Micro 820 controller, Panelview 800 and...
3,064
I have an allen Bradley micro running a fan in an industrial paint mixing facility. The input fuse is 3a. The system will run fine for a bit and...
1,992
Found a couple of old unused Micro 810s with lcd displays in the miscellaneous section. Don't ever use ccw or indeed any Allen Bradley, but...
4,189