allen bradley problem
thewimpieman
Mar 2012
sneek
hello
i have a problem white my ab plc5-80 i have connected it by a 1785 enet slide and rs linx can see it but if i try to connect it in rslogix5 it keeps giving me a error "diagnostic status failed sts= 0x20. can someone plz tell me what that problem means and how i can fix it
greets
I think that the same error message can appear if the switch # 8 (the bottom-most one) in the chassis backplane is set to ON. This sets the memory on the CPU to be protected. Had this happen once and I got the "diagnostics status failed".
Apart from that I agree with Mickey that the least errorprone way to get online is to use the "Comms" ... "System Comms" menu item in RSLogix, and then browse and select the CPU, and then activate "online", "download" or "upload". If you chose download, you will probably be prompted to merge with an offline project.
I have 1769-IF4 module and 1766 micrologix 1400 series B controller, when connecting Analogue input in module it's showing maximum values of...
1,692
We have an application with an Allen Bradley servo driving a rotary table. During normal operation the servo positions perfectly (within 0.001...
2,287
Hello everyone, I face a problem with setting connection between my computer and PLC using NAT addressing. I configured NAT. In private network...
2,006
Hello, I have a drive allen bradley powerflex70 that works normal it shows that it has start and frequency variation but there is no output 0...
2,119
Above mentioned HMI is installed in my plant with Micrologix PLC. Yesterday the HMI suddenly stopped working during plant operation and HMI's...
4,941