ALM function block programming
remullis
Oct 2012
Georgia
179
I am new to function block programming and would like to know how to change setpoints for say HiLimit, LoLimit, etc. I am using RSLogix 5000
Hi
In the alarm AOI "ALMA" which is the one I think you are talking about the tag that you have created in the ALMA just right click and and press Monitor. This will ring you to the tag and now look for "Your tag name".HLimit
This is were you can adjust it
Donnchadh
Thanks, just that simple, geez! I was thinking I should be in "edit" tags, but it was in a read only state, in monitor tags I was able to adj the setup point. Thanks again.
Rich