Analog Input Fuses
maverick33
Dec 2005
USA
36
Hello all,
I just have a couple of questions regarding fusing of analog inputs...
Background:
I am in the process of commissioning and testing some new equipment from Europe that uses AB Control Logix with 1756-IF16 analog input cards with pretty much everything wired single ended. The inputs also go through barriers (MTL 7087+) due to Class 1 Div 2 hazardous location requirements.
Problem:
Occasionally some of the inputs spike to maximum for no apparent reason. This seems to be isolated to temperature transmitters (4-20 mA) that all of a sudden max out for no apparent reason. Checked the sensor and wiring and everything checks out up until a small 32mA resistive (don't remember how many ohms at the moment)fuse that is just before the card input.
I have been able to resolve the problem by removing power to the barrier cards temporarily and then reapplying it. This seems to work but the problem still occurs ay completely random intervals. I had not seen this type of resistive fuses but have heard through the grape vine that these are often used with Siemens analog input cards. I don't have any Siemens experience and was wondering if anybody could confirm this?
I inquired with AB about potential problems with these fuses but they were unable to help. I removed these resistive fuses and the sensors seems to be working without any problems now but I am still just curious as to if anyone else has seen/used these before?
Thanks.
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,146
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
261
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
120
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
88
Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
112