analog inputs for RsLogiX 500
tsaronja
Aug 2006
zagreb
hi! can anyone describe how addresing analog inputs in ladder diagram for RsLogix 500 and which symbol use?? i am new in RsLogix, till now i was working only with Simatic Step 7.
for example, in simatic step 7 analog inputs are addresing with AIW0, AIW2, AIW4... etc, and use symbol "MOV_V" for moving analog input AIW to variable word(example "VW100).
Thank You very much!!
If you were using a 4 channel analog input card (1746-NI4), and it were placed in Slot 1 in your SLC rack, then the four channels would be addressed as I:1.0, I:1.1, I:1.2, and I:1.3.
Here are two examples. The first example uses the compute (CPT) instruction to read the value from the input card (I:1.0), add an integer offset, and then divides by a floating point value to result in a transformed value - position in this example.
In the second example the scale with parameters function (SCP) is used to read the value from the input card (I:1.1) and scale the value to a floating point output.
To define a symbolic name for each channel, open the input data file, highlight the address (I:1.0 for example), and then type in a name in the Symbol box.
also if you download the manual for a particular analog input card it will provide all the information you will need on programming for that card including some good examples
Hello, I'm new to RSLogix 5000, used to RSLogix 500. Is there a command similar to SCP in RSLogix5000?, or what should I do? I'm currently using...
7,127
I've got a slc 5/03 and the 1746-FIO4V card= 2 Input (V or mA) and 2 output (0-10 vdc) and am setting up an analog output in RSLogix. If so, I...
9,649
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
76
I am converting a SLC 500 to a Compact Logix. I plan on using a Compact Logix 5380 with conversion Kit. The problem is that the analog input cards...
161
Hi there, I'm doing some extensive testing and commissioning with a slew of new Emerson PACSystems RX3i PLCs. It would be convenient to...
200