Analog Module FX2N-4AD
jcp
Feb 2010
Multan
369
Hello friends;
I am confusing to connect the channel of FX2N-4AD with rosemount Transmitter model 3051.
I want to read 4-20mA from the transmitter.
I jumper the V+ and I+ on module.
I connect -ve of transmitter to VI- on module.
and positive of transmitter on V+ and I+ (Which is jumper)
But the transmitter is not powered. I check the voltage on V+ and I+ on module there is no voltage.
How i connect the 2 wire transmitter with FX2N-4AD?
Regards
I have wiring diagram of analog-digital module (FX2N), can you please post the wiring diagram of the transmitter?
I can't seem to get you on this statement:
I'm not sure what you mean by 'the transmitter is not powered.' That's why I want to see the wiring diagram.
re-edited version:
As you indicated the Rosemount transmitter is a 2 wire loop powered device, it needs 24Vdc power supply.
There's a 24(+) and 24V(-) terminal at the top of the rows of wiring terminals on the FX2N
You need to connect:
FX2N 24+ to Rosemount (+)
Rosemount (-) to FX2N V+
Jumper V+ to I+ (like you've done)
FX2N VI- to FX2N 24-
I am using FX2N-5A Mitsubishi analog module. My application is to read the vacuum pressure level with the help of transducer sensor and by analog...
1,684
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
130
Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
124
In this sample programming, what does U4 mean? Any assistance would be greatly appreciated.
297
I have run into a problem with my first time installing a 2080-OF2 module on a Micro820 and have a hunch that the module itself - brand new out of...
955