Analog output issue
phil hughes
May 2005
31
We are sending a setpoint to our Ozone generator using a 4-20mA signal from a SLC5/05 NO8I Output card .
The Wedeco Ozone generator receiving the setpoint has a Automation Direct PLC DL250-1 PLC -analog Input card is a F2-O4AD-1.
The system has been in use for 10 years . We have just started experiencing an unstable setpoint at our generator, the SP floats high and low then returns back to normal on random occasions . I used a Fluke 772 mA clamp meter to determine if the signal coming from our SLC is stable -it appears to be rock solid.the 24v power supply is perfect. Both ends of the belden are grounded.
No recent wiring modifications have taken place.
My question is ; I dont know whats going on ? is it noise the my clamp on meter can not detect interfering with the Automation direct PLC input .
Any help would be appreciated
Do you have Direct Soft software to observe the value in the D250 and RSLogix 500 to look at the value in the SLC?
A scope is a better tool to check for noise than a clamp-on ammeter.
Generally you only ground the shield on one end, not both.
Ah ok I'll take one ground end off the belden .Also I have both software packages , i'll observe both SLC and Automation Direct analog signals . We also have a scope we can try . thanks for the reply !
Scope is a voltage input. You’ll have to look at the voltage drop across a resistor to see what current is.
Connecting across the (+) and (-) of the analog input is probably the easiest way.
Use an LT comparison and a holding register to save the lowest value that the DL is seeing while it operates. Then you can come back later and see if its actually getting a droop in the analog signal.
+1 to Steve's single ended ground comment. loops will drive you nuts.
I have added isolators to 4-20 signals before to test for ground loops. Essentially 1:1 transformers they have shown me where a loop exists and I can trace it from there. Sadly they have been left there occasionally as time didn't permit other options.
Hello, As you may remember, I posted in January about an issue we were having with our micro850 controllers (2080-LC50-48AWB) to operate...
4,300
Hello, We are using 80 micro850 controllers (2080-LC50-48AWB) to operate irrigation booms in our nursery. We are using an analog output card...
7,281
My 1771-OFE analog output card was previously configured to Voltage output OFE1 (voltage version), all four channels are 0-10Volts corresponding...
18
7,219
Hi all, Playing around with this controller for a future project. Background: Micro 820 with 1 analog voltage output. Discrete on/off to enable...
33
6,765
Greetings, I'm about to begin a new job taking on a major operation drive by controllogix processors and tons of flex I/O modules.... its a big...
2,948