In general, the CompactLogix is the "Originator" and the Anybus is the "Target".
Assuming the Connection Points shown by the Anybus webpage are correct:
When the Originator sends data to the Target, that's considered "Output" data and should be Assembly 160.
When the Target sends data to the Originator, that's considered "Input" data and should be Assembly 165.
Try swapping Assemblies 160 and 165 between the Input and Output fields for the Connection Parameters tab of the Generic Ethernet Module object in the Studio 5000 I/O tree.
Also, I notice that the datatype includes both a ConnectionFaulted BOOL subelement and the data payload.
Try adding 4 bytes to the Input connection to account for the Connection Status.
Try disabling the Connection Status (this is probably in the Comm Format pull-down) and keeping the I/O sizes the same.