Anyone here have Bosch experience?

Lovell

Lifetime Supporting Member
Join Date
Feb 2013
Location
Saskatchewan, Canada
Posts
120
Hi all,

I am experienced with Rockwell by have recently encountered a Bosch PLC. It’s an IndraControls XM21 V14. I installed the software and logged in with the most recent PLC file open. It gave me a warning that there are differences and my options were to download or abort. In Rockwell download means overwrite PLC. Does anyone know what it mean in Bosch PLC. I could not go online, there does not seem to be a correlate option.
 
Never worked with XM2 but I think it should be Codesys V2.3 platform. It means overwrite. You can backup/read project (Online-Login then Read file from PLC).
 