Hi guyes anyone who can give me a hint
i have done following program
l #Byte_nr
slw3
lar1
opn #DB_NR1
l db1.dbb1
l 1
==i
= m 10.0
A [Ar1,p#1.0]
jc db2
JN end
db2: opn #DB_NR2
l db2.dbb0
t #counting_value
end: nop0
And i get a cpu stop, and when i read in the Module information i can see this: Help on Event 2x24
Cause:
You have used an illegal address range for area-crossing indirect addressing. The area ID of the access address (bits 24 to 31) is not permitted.
To correct or avoid errors:
Use a pointer with a correct area ID.
How does a permitt the bits 24 to 31 ?
If you do not specify the area in AR1, you must specify it in the instruction, your code needs to be:
Code:
A [b]DBX[/b][Ar1,p#1.0]
When in the STL-editor, press F1, click on index, on new form click on find, enter "indirect", wait till it's done searching, then look for: Example of Area Crossing Register Indirect Addressing.
Pretty nice example of something similar.
Just can't seem to figure out why you:
OPN #DB_NR1
L DB1.DBB1
or
A [AR1,P#1.0]
jc DB2
jn end
DB2: .....
Easier to just make it:
A [AR1,P#1.0]
jcn end
DB2: .....
But thats just cosmetics, what L D said should fix your problem...
Thanks again L D.
i Should think about that you whas writing Jeebs, i have recently start with indirect adressing so all hints a can get i would be more than grateful.
Berra
On another note, in this bit
Code:
 opn  #DB_NR1
 l	db1.dbb1
You open #DB_NR1 data block, doesn't the next instruction open the data block DB1.
Ok there is someting more i don´t get
When i do like this
l #byte_nr (1)
slw 3
lar1
opn #db_nr
a dbx[ar1,p#0.0] (why does this bee 1 in the RLO?)
jcn end
a dbx [ar1,p#1.0](and why is this 0 in the RLO ? i thougt this should bee 1)
jcn end
jc b1
b1: l db2.dbb1
t #counting_value
In my project i use an Anybus-X gateway for exchanging data with 3rd party as a modbus slave. Data is provided as means of PIW and PQW area and...
5,897
Hi everyone, I hope you're all doing well. I'm currently working on updating an HMI project for the GP2500, and I've encountered a bit of a...
126
Dear colleagues, hope you can help on that matter. We have a project where we need to control 3 servomotors to move a auger feeder system...
38
1,218
Project involves updating a ~23 year old controller (C200HX CPU64). The HMI is a windows NT machine with the gui done with Delphi 5 (Pascal)...
1,121
Hello, I am looking into a robotic sanding and grinding project where we would need area scanners. I just spoke with OMRON and they say that their...
1,511