In my system, I have one Nokia 30 GSM modem which is connected with SLC 5/03 on Channel 0 - User Mode.Another Nokia 30 GSM Modem is connected with PC. I can send message from PLC to any mobile. But now i want to read Message in PLC, which is sent by any mobile ( It may be data enable or may not).It will be possible through ASCII read Instructions. I think with ARL instruction. I tried but failed. So if any one had tried and got success or has any idea about this than kindly send me the codes or any suggessions. It is not necessary that it should be Nokia 30 GSM modem. It may be any data enable modem.
You can use the AT+CMGR=y <CR> command (where y=the memory location where the message is stored)
You will probably have to write some code to repeatedly scan or check the port for an incoming message.....
Hope this helps ;)
I did something like this to read a keyence vision system serial port through ch0 on a PLC5. It ended up being quite a bit of trial and error to establish and maintain communication. Once I got the channel settings figured out, I had to send a particular string to start the vision system communication, then read the string and parse and convert it to integers. I'll attach the example, but your application is surely much different.
It sounds like your channel configuration is all working. You just need the logic to go with it. You may need to use the ABL, ARL, AEX, and AIC instructions like I did ...
Good morning to all, I need to modify an existing PLC MIcrologix 1500 configured with a Modem on Channel 1 (DF1 Full Duplex) and an...
1,443
I am working on a project, inside an AB CLX, I implemented the Modbus TCP Client AOI published on AB website, to interreact with a Modbus ASCII...
3,599
PLC is ControlLogix 1756-L73 CPU with firmware 28 In the PLC the value for A60[110] is "AT", Style ASCII, Data Type INT. In KEPServerEX I tried...
1,583
Hi all, this is the first time I have posted on here, I have been reading with interest for a few years now. The problem I have is regarding...
1,528
I have a micrologix 1200 and I am trying to get a barcode scanner to talk to the COM 0 port. I know the scanner baude rate is 9600 because I...
1,789