Beckhoff and CitecScada

Hoang Minh Vy

Member
Join Date
Jan 2014
Location
BRVT
Posts
4
Dear Bros,
Does anyone used to configure communication between Beckhoff PC and Citec Scada V5.41 (or higher).? Please give me some document or instruct me how to choose config or protocol to use
Thanks very much.
 
You can use ADS to communicate with BECKHOFF PLCs from CITECT. It is very simple you should just choose TWINCAT in Board Type (Boards section In Communications folder) and type the AMS NET ID (Beckhoff device address) in Special Opt (Ports section in Communication folder).
The only Point is you should type the address of your device just like the following example:
Assume that device address is :192.168.0.101.1.1
You should type this in Special Opt:AMS192.168.0.101.1.1

After this you have access to the logic variables with Address
 

Similar Topics

Hi, I'm trying to import a Rockwell/AB EDS to Beckhoff but I'm not sure how to import/install the EDS. It is a PowerFlex 525 EDS. Is there a way...
Replies
1
Views
99
I'm trying to integrate a Beckhoff IPC with a Controllogix PLC. There is some documentation, on the Beckhoff website, on how to do a PLC-PLC comms...
Replies
0
Views
103
Hi everyone, This is my first time posting, so please forgive any omissions or mistakes. I am attempting to control the velocity of a stepper...
Replies
18
Views
1,072
Hello sameone have Beckhoff PLC Siemens Sinamics V90 configuration example?
Replies
0
Views
107
hello, I am using Beckhoff with TwinCAT3 and when I change or add some new hardware or for any reason, there is a mismatch in the real hardware vs...
Replies
1
Views
140
Back
Top Bottom