Sergijk0
Member
Good afternoon!
I have problem with connection 3d-party device to beckhoff CX8090. The device is Festo CTEU-EC module(EtherCat).
After auto scan for I/O in TwinCat 2 I every time have an error: “invalid index offset”. After that error the Festo module is visible but I cannot to activate config or to do scan one time more.
The Festo module is connected to X102 port. The ESI file for Festo module is copied to “C:\TwinCAT\Io\EtherCAT” folder on my PC.
I connect my PC to PLC via X001 port. I thought that it was the problem of Festo module but then I connected other device (Staubli robot) and the problem was the same.
When I connect Beckhoff EP23xx modules to PLC everything is Ok.
Have somebody seen similar errors?
I attached log messages for System manager. I don`t know why but first error is not here.
The first error is “Init10\IO: Create TComObj PREOP >> AdsError:1795 (0x703, ‘ADS ERROR: invalid indexOffset’)”
Also I attached .tsm file which I have after scanning and errors.
Thank you very much!
I have problem with connection 3d-party device to beckhoff CX8090. The device is Festo CTEU-EC module(EtherCat).
After auto scan for I/O in TwinCat 2 I every time have an error: “invalid index offset”. After that error the Festo module is visible but I cannot to activate config or to do scan one time more.
The Festo module is connected to X102 port. The ESI file for Festo module is copied to “C:\TwinCAT\Io\EtherCAT” folder on my PC.
I connect my PC to PLC via X001 port. I thought that it was the problem of Festo module but then I connected other device (Staubli robot) and the problem was the same.
When I connect Beckhoff EP23xx modules to PLC everything is Ok.
Have somebody seen similar errors?
I attached log messages for System manager. I don`t know why but first error is not here.
The first error is “Init10\IO: Create TComObj PREOP >> AdsError:1795 (0x703, ‘ADS ERROR: invalid indexOffset’)”
Also I attached .tsm file which I have after scanning and errors.
Thank you very much!