Best kind of Fuse for a PLC?
wlr3m4
Oct 2017
Saint Louis
28
I've got a small project where we are moving a PLC from a non-enclosed setting to a cabinet and I want to put a fuse on the incoming 120VAC.
I've got a 1756-PA72/B and I'm wondering what kind of fuse would be best for it.
That power supply only draws less than 1 amp while running, but the inrush current at startup is 20 amps. I would use something like a 5 amp D curve UL1077 circuit breaker for it.
I only have a 1756-L61 and 1756-ENBT/A attached to it, will both of those still draw less than an amp of current?
I found this:
https://www.alliedelec.com/eaton-cutler-hammer-wmzs1d05/70058833/
Which is a UL1077 breaker, but its 277/480VAC rated, I can't find a single pole 120VAC breaker...
The voltage mentioned is the highest voltage on which you can use it. You may always use fuses at lower than specified voltages. It's the same as with wiring: you don't doubt using cable specified for 400Vac on 24Vdc because you're sure it can handle that voltage.
I've got a PLC that I'm going to read a signal from a source at 24-30VDC @ 2A but my PLC can only take 1A on its input signal. I want to get a...
3,246
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
505
I have S7 1512C controler for controlling 48 PID temperature loop, the output is PWM. Please I need the best, most efficient way to write the...
619
I am going to need to use HART multi-drop in order to handle a series of Vega Radar units. There are a lot of options and I'm wondering what...
262
Out of interest, I'd like some thoughts on what would be considered best practice with regards to a 2-position turntable control scheme (see...
17
1,154